Cable group derating factor

rated by 0 users
This post has 1 Reply | 1 Follower

Top 100 Contributor
Posts 2
skgajjar Posted: Fri, Dec 18 2009 3:47 AM

IEC 60364-5-52 (2009), Table B.52.20 shows the derating factors for maximum 9 numbers of cables per tray or ladder. Does this mean that maximum allowable cables in single cable tray can not exceed 9 ?

Is there any other IEC standard that provides the group derating factors for more than 9 LV cables run in single cable tray ? Thanks.

Top 10 Contributor
Posts 486
Steven replied on Sun, Dec 20 2009 1:32 AM

I don't think the intention is to limit to 9 cables.  For 9 or more cables I think the intention is that you use the derating for 9 - i.e. this would be the maximum worse case factor to apply.